Ah, they are both found towards the bottom of the list, when configuring the telegram. The address are actual fault code and actual alarm code. They do not have addresses that the PLC can see yet, I use DP_RD to update a db. After seeing that example I mentioned.
I know that it is necessary to change the telegram e, but what addressing the investor conveys an error. I have an electrical cabinet far from the panel and therefore I need to see the inverter error number
Hi, change to the free telegram, or to a telegram that has it ready. There does exist an application example on this. The example has the full Sinamics G120 alarm and fault details as text lists in the HMI, which is pretty cool.
Ah, they are both found towards the bottom of the list, when configuring the telegram. The address are actual fault code and actual alarm code. They do not have addresses that the PLC can see yet, I use DP_RD to update a db. After seeing that example I mentioned.
I know that it is necessary to change the telegram e, but what addressing the investor conveys an error. I have an electrical cabinet far from the panel and therefore I need to see the inverter error number
Hi, change to the free telegram, or to a telegram that has it ready. There does exist an application example on this. The example has the full Sinamics G120 alarm and fault details as text lists in the HMI, which is pretty cool.