At first I thank Hegamurl for his great video tutorials.
I am doing my first safety program with TIA Portal and S7-1200F PLC. At the moment I do not have any physical PLC and my simulation do not work with my fail safe application.
I have searched information about F-DI SM1226 (16 input) module configuration, but still I do not have a clear view about the issue; is it possible to use the all 16 channels separately. Let's say I have SIL 1 and do not need double channels. So can I wire one sensor to e.g. input 0 and just a different device to channel 8 and the inputs works separately? Is it configured with 1001 evaluation and still keeping the both channels marked "active"?
Thank you Pascal for your response! I finally got a fail safe hardware to my hands and it really seems to be just as you mentioned. When using 1001, the channels work separately also in F-DI SM1226 module. :)