Hello,
I have an backup issue with one of my systems. Pls help...
The original system was made with 6ES7511-1AK00-0AB0 and TIA V13. A few months ago the CPU had broken and had been replaced with actual type 6ES7511-1AK02-0AB0. The project wasn't upgraded to V15, because the CPU is backward compatible and can run TIA 13 blocks. Unfortunately, the original project has disappeared/deleted and I want to make a backup.
I had tried all tricks from your video (Hegamurl) and from Siemes site also, but no luck ( Upload as new station, new project with undef. CPU, Compatible project works just from earlier version to V13.1, etc)
The TIA 13 haven't support for new CPU, TIA V15.1 can't download V13 blocks
With Compare function (online/offline) I got the Program blocks from CPU, but hw config is still missing. On Profinet are connected 3 pcs ET200SP with many IO modules.
Any idea or solution is welcome.
Hello,
Yes, I had read the SMC with TIA, but I saw just the program blocks. The hardware config is also important, because on each of these ET200SP are 10-15 IO card, 5-6 of them are analog IO. Setup of these cards are also important.
When I'm online (accessible devices) I can see the IP addresses of each interface module.
I may make the same hardware configuration and try to setup modules based on schematics and program. This should take a lot of time and effort , but the result won't be 100 % for sure.